Hello,

we have an old Kabola, the E7 model, on our boat. We have yet to get it running. 

We know that the diesel is reaching the regulator fine and the boiler lights but it burns out very quickly, after a few minutes. When I look at the parts inside the boiler and compare with the photos in the instruction manual, it looks like there might be parts missing. 

 

Can anyone with experience of using one of these boilers advise?

photos below comparing our boiler with the pictures in the manual. 

 

Many thanks 

IMG_2172.JPG

IMG_2173.JPG

IMG_2174.JPG

IMG_2176.JPG

IMG_2177.PNG

Link to comment
Share on other sites

The only part missing is the sealing 'rope'. I have purchased some from Karunda and tried to fit it to an ODE4 but without success.

The fire works without it and I checked with a Karunda recommended fitter who said it was not needed.

Your fire needs a good clean, hoover out and check the carb. carefully especially the filter (see KK's guide), sounds as if you have some oil supply problems.

Take care when cleaning the  burner pot - don't damage the thermal shunt where in projects into the combustion chamber - the fire won't run if this is broken.

Check the seal around the oil inlet, the colour variation on the exterior of the burner pot (pic 4) is unusual.

They are good units and when set up properly burn happily.

L,

Edited by LEO
Link to comment
Share on other sites

3 minutes ago, Jo Green said:

Thank you Leo. That's really useful. Hopefully we'll have it running soon. 

Do you know if this little plate on top of the catalyst is necessary? 

KK has run these units without a catalyst so it should run without the plate..........you can get new cats. from Karunda but they are about £80.

I do think you have problems with fuel supply, have you checked the filter?.

I suspect someone has 'modified' the ring '12' to make re-fitting it easier and sit 'flat' they should have a small 'lip'

I got a new one from Karunda last year - not too expensive.

I have had my OD4 for 12 years now and only just learned the secret of trouble free lighting it - use less meths, make sure there is enough fuel in the bottom of the burner pot and don't keep lifting the lid to see if the fire is Ok.

L.

 

Link to comment
Share on other sites

How long has it been since it was last used?

If it has been several years, the oil in the regulator can evaporate, gunning up the tiny slot in the regulator through which the oil drips into the burner pot.

My OD4 stove hadn't been lit for 7 years and tbe inside oftheregulator was covered in a sticky film of oil diesel. I ended up using brake cleaner to remove it.

After some initial problems with it over fuelling, cured by carefully adjusting the high flame setting, it has worked perfectly and starts easily using a 50p piece sized pool of oil in the base and 2 capfuls of meths.

Link to comment
Share on other sites

Hello, 

One thing I forgot to mention- we never saw the thermal shunt supplying fuel. It stayed dry and seemingly untouched by diesel each time we lit it even when we had the button of the fuel protection device depressed.

Should fuel have been dripping from this nozzle? 

Working on the theory that this pipe could be blocked we sought to clean it out but unfortunately broke it. (See picture).

We've established that the fuel is flowing into the regulator fine from the daytank and the filters aren't blocked. The regulator is definitely working and allowing fuel to flow through.  

 

Any advice? 

 

Thanks! 

image.jpg

image.jpg

Link to comment
Share on other sites

Err no, this unit only operates by expansion to keep the fuel supply valve open. It's temperature sensitive and needs heat to open the valve. If the flame goes out it will shut off the valve, stopping fuel flowing into the burner pot.

Spares are available from Karunda.

The fuel drips into the burner pot much lower down, there is a pipe from the carb. connecting to this.

Link to comment
Share on other sites

As others have explained that is the thermocouple, which is the flame failure device.

It needs holding in for 30-90 seconds after the stove is lit so that fuel can flow until the thermocouple is hot enough to stay open on its own.

The fuel drops into the bottom of the stove, near the "L" shaped plunger, which is vigorously pulled in and out and twisted at the same time occasionally, to clear burnt crud to allow oil to enter the stove.

If you take out the catalyst, turn the regulator to setting 2 and press the thermocouple overide, you should see oil entering and gradually flowing over the floor of the stove.

When the pool of oil is about  the size of a 50p piece, release the thermocouple overide and add 2 capfuls of meths to the pool of oil.

Put the catalyst back into position and drop a lit match in and wait until the flames begin to die off.

Press the thermocouple overide for 30-90 seconds, then release it. The stove should stay lit.

After 15 minutes turn the regulator to the desired position (usually between 1&3) and away you go.

It is an easy DIY job to change the thermocouple if necessary.

Link to comment
Share on other sites

Thank you. I've ordered a new thermocouple from Kuranda. Hopefully when that arrives and is fitted we might get it lit. I think there is too much of a build up of soot and oil in the bottom of the burner pot so need to get that sorted too. 

Cuthound- we have no markings on the regulator as it's old and worn. Whereabouts is position 2, do you know? 

Link to comment
Share on other sites

The regulator turns anti-clockwise from off through "pilot" then 1-6.

There is some resistance to overcome from off to pilot, then it moves smoothly.

I find anything over setting 4 gives increasingly yellow flames, however in practice setting 1 or 2 cope with sub zero temperatures, giving internal boat temperatures between 23°C and 29°C.

I dont know how hot it would ultimately get on higher settings as 29°C is too hot for me in a 60 foot narrow boat. :blush:

Stick with it, when working properly these are fantastic little stoves, much cleaner and more easily controlled than wood or coal fired ones.

At the current diesel cost of about 60p per litre, mine costs about £24 per week when left on 24/7, so about the same as two bags of good quality coal.

 

20171106_100431.jpg

Link to comment
Share on other sites

Hello, 

the Kabola is working and bringing much needed heat! We are over the moon! 

One more question- the main radiator is only hot at the bottom so presumably needs bleeding. With a pressurised system can I just go ahead and bleed to radiator? The last system I had (a mikuni) had a header tank so I could easily add more water to the system. How does it work with a sealed and pressurised system? 

 

Thanks in advance,

Jo

Link to comment
Share on other sites

3 hours ago, Jo Green said:

Hello, 

the Kabola is working and bringing much needed heat! We are over the moon! 

One more question- the main radiator is only hot at the bottom so presumably needs bleeding. With a pressurised system can I just go ahead and bleed to radiator? The last system I had (a mikuni) had a header tank so I could easily add more water to the system. How does it work with a sealed and pressurised system? 

 

Thanks in advance,

Jo

Great news about the Kabola.

With a sealed and pressurised system, the pressure will force small amounts of air out.

This will result in a pressure drop for the system. If the pressure has dropped too low, you will need to refill the system by attaching a hose, connected a CRT water tap or other pressurised source of water,  to the fill point on the system (usually two taps in series aka as double check valve) and filling until the system pressure gauge shows the correct pressure. 

Link to comment
Share on other sites

  • 3 weeks later...

Hi,

Thanks for all your previous help. We currently have the Kabola running. It’s easy to light and runs well, heating three radiators in the boat. Radiator one is small and the highest in the system. (See pic 1) It sits in the engine room, near the Kabola. Radiator two is larger than the other two put together and sits midway down the boat. Radiator three is small and towards the bow of the boat. Radiator one and three heat up quickly from top to bottom and seemingly have no air inside. Radiator two is quite obviously only half filled with water. You can clearly feel the heat ends about half way up. 

We have studied the system and we think we’ve found an expansion tank (see pic 2); a pressure relief valve (see pic 3); a temp and pressure gauge (see pic 4) and seemingly no fill up point. (Possible fill points- see pics 5, 6, 7.)

The pressure gauge indicator never leaves zero whether the boiler is running or not but the plumbers tape where it connects to the Kabola looks new and the gauge looks like the newest part of the system. (I’m hesitant to believe it’s not working.)

Please excuse the slighty rambling description. I’m trying to communicate everything as clearly as possible. Is it possible, given that the system seems to be only 60% full of water, that the pressure gauge is working fine but there simply isn’t any pressure in the system? 

We can’t locate any obvious fill up point (certainly not two check valves in a row.)

What would the risks be in seeing if radiator 2 wants to bleed air? 

Your advice and help is much appreciated.

Jo

9153E7F2-3BCB-4039-A7D2-1B98B2C74089.jpeg

33B636B1-104A-48D5-A7B0-58DE24EB5D80.jpeg

866D2AEA-F58F-40C9-8136-E988D6298CA4.jpeg

EA1D9519-77F3-4A41-B16D-9CB812390676.jpeg

A02602E2-5392-4D55-882B-B0F9F087448A.jpeg

F7CE3357-B6BF-44AD-BC9D-49FB591D1A91.jpeg

D0399287-485B-48B0-9BF6-F3D955ACB98D.jpeg

Link to comment
Share on other sites

What is shown in Picture 5 is surely a 3 BAR pressure relieve valve.

As Rusty says, Picture 3 is, I believe, an automatic vent valve.

My E5 boiler had a PRV directly mounted low down on the boiler, and sales material I have seen implied it was an original fitment.
 

 

Link to comment
Share on other sites

Pic 7 looks like the fill point. The cap on the end will remove to attach the hose.

Before removing though it looks like you may have to turn the valve off on the top to stop water coming out. A normal fill valve will shut this off automatically 

It doesn't look like a standard fill valve though so a close up pic would help.

 

Pic 2 Is an expansion vessel/tank

Pic 3 Auto air vent

Pic 4 Temp and pressure gauge

Pic 5 Pressure relief valve. I would run a pipe from this to a safer point. If this ever activates hot water will come out. Also if the black knob is turned by someone accidentally they might get a shock.

Pic 6 Is a lockshield Radiator valve. used for adjusting the flow of water through the radiator. Don't touch these can leak if messed with.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.