I HAVE JUST PURCHASED A BANK OF NEW DEEP CYCLE BATTERIES.

THEY ARE ATTACHED TO A MASTERVOLT INVERTER/CHARGER.

ALL THE POSITIVE STRAPS ARE A DIAMETER OF APPROX. 16MM.

I AM FITTING NEGATIVE STRAPS OF SAME DIAMETER EXCEPT FOR ONE (200mm long) WHICH IS IN MY TOOL BOX BUT IS ONLY APPROX 7MM DIAMETER.

BEING ON THE NEGATIVE SIDE OF THE CIRCUIT IS THIS GOING TO BE DETRIMENTAL??

Link to comment
Share on other sites

It is better to have all cables of the same size and length. How big is your battery bank? Do you know what size your cables are in mm2?

Sound like 35mm2. Your smaller cable sounds much too small and will potentially be dangerous.

Edited by MHS
Link to comment
Share on other sites

I HAVE JUST PURCHASED A BANK OF NEW DEEP CYCLE BATTERIES.

THEY ARE ATTACHED TO A MASTERVOLT INVERTER/CHARGER.

ALL THE POSITIVE STRAPS ARE A DIAMETER OF APPROX. 16MM.

I AM FITTING NEGATIVE STRAPS OF SAME DIAMETER EXCEPT FOR ONE (200mm long) WHICH IS IN MY TOOL BOX BUT IS ONLY APPROX 7MM DIAMETER.

BEING ON THE NEGATIVE SIDE OF THE CIRCUIT IS THIS GOING TO BE DETRIMENTAL??

YES

 

Oh and 16mm is too small unless your mastervolt Combi is a very small one. Oh but wait a minute, you say diameter, do you mean diameter? Normally we talk about the cross sectional area of the cable (not including the insulation. So can you be more precise - 16mm diameter or area? Including or excluding the insulation?

Edited by nicknorman
Link to comment
Share on other sites

I HAVE JUST PURCHASED A BANK OF NEW DEEP CYCLE BATTERIES.

THEY ARE ATTACHED TO A MASTERVOLT INVERTER/CHARGER.

ALL THE POSITIVE STRAPS ARE A DIAMETER OF APPROX. 16MM.

I AM FITTING NEGATIVE STRAPS OF SAME DIAMETER EXCEPT FOR ONE (200mm long) WHICH IS IN MY TOOL BOX BUT IS ONLY APPROX 7MM DIAMETER.

BEING ON THE NEGATIVE SIDE OF THE CIRCUIT IS THIS GOING TO BE DETRIMENTAL??

 

 

NO NEED TO SHOUT...

 

As others have said, yes, but how detrimental depends on the maximum inverter power you will ever use. What rating is it?

 

Welcome to the forum, by the way!

Link to comment
Share on other sites

 

 

NO NEED TO SHOUT...

 

As others have said, yes, but how detrimental depends on the maximum inverter power you will ever use. What rating is it?

 

Welcome to the forum, by the way!

He wasn't shouting he was typing in block capitals. Much easier to read on a phone screen with mince pies like mine.

Yes welcome to the forum.

Link to comment
Share on other sites

But that is the equivalent of SHOUTING...

It used to be. With more people using phones these days, many things will change. Replies will tend to be more curt too, like this one :)

Link to comment
Share on other sites

It used to be. With more people using phones these days, many things will change. Replies will tend to be more curt too, like this one smile.png

 

 

Disagree.

 

Lots of people read this forum and post without using caps. It's not necessary and its poor internet etiquette.

Link to comment
Share on other sites

 

 

Disagree.

 

Lots of people read this forum and post without using caps. It's not necessary and its poor internet etiquette.

To disagree is your privilege. Maybe not necessary for you, but not everybody has eyes like mine. Many things are poor "internet Etiquette" yet this one gets picked on with boring monotony. Why?

Edited by Guest
Link to comment
Share on other sites

YES

 

Oh and 16mm is too small unless your mastervolt Combi is a very small one. Oh but wait a minute, you say diameter, do you mean diameter? Normally we talk about the cross sectional area of the cable (not including the insulation. So can you be more precise - 16mm diameter or area? Including or excluding the insulation?

I'm assuming they're 16mm diameter including insulation, so say 12mm diameter copper. That's approx 35mm2.

So the single 7mm diameter cable is say 5mm diameter copper or approx 15mm2. Definitely not going to be sufficient.

Edited by MHS
Link to comment
Share on other sites

This picture shows why you really dont want to use undersized cables on an inverter.

Cables are 25mm squared, was fused (way too big a fuse ) , tidily installed and had even been in use for quite a while.

I would check the manual (should be easy to find one on the Mastervolt site) and follow Mastervolts install instructions for your size of inverter.

post-7857-0-91251400-1486251189_thumb.jpg

Link to comment
Share on other sites

I'm assuming they're 16mm diameter including insulation, so say 12mm diameter copper. That's approx 35mm2.

So the single 7mm diameter cable is say 5mm diameter copper or approx 15mm2. Definitely. It going to be sufficient.

 

 

Actually its impossible to say without knowing the maximum current the link will carry, and the voltage drop the user finds acceptable.

Link to comment
Share on other sites

This picture shows why you really dont want to use undersized cables on an inverter.

Cables are 25mm squared, was fused (way too big a fuse ) , tidily installed and had even been in use for quite a while.

I would check the manual (should be easy to find one on the Mastervolt site) and follow Mastervolts install instructions for your size of inverter.

 

You're not kidding!

Link to comment
Share on other sites

 

 

Actually its impossible to say without knowing the maximum current the link will carry, and the voltage drop the user finds acceptable.

I have edited my previous post. Auto correct managed to add a full stop and remove one important word "Not"

 

BSS recommends 25mm2 as a minimum. No point going smaller than that.

Edited by MHS
Link to comment
Share on other sites

The op described his cable as 7mm diameter. Assuming that is the copper diameter it will be 35mm2.

The max current capacity of that cable depends upon how good the ventilation is and the ambient temperature - cable current rating is based upon the cable overheating. Anyway assuming it is in the engine space which is warm to hot and assuming the cable is in free air, I would guess the max current will be about 80A.

 

80A at 12V is 960W, so an inverter over 1000W will overload the cable, not to mention the other DC loads on your boat.

 

You need to consider if the cable is big enough. Also the main fuse must be below the 'weakest' cable capacity in your circuit, so check that as well.

Link to comment
Share on other sites

The op described his cable as 7mm diameter. Assuming that is the copper diameter it will be 35mm2.

The max current capacity of that cable depends upon how good the ventilation is and the ambient temperature - cable current rating is based upon the cable overheating. Anyway assuming it is in the engine space which is warm to hot and assuming the cable is in free air, I would guess the max current will be about 80A.

 

80A at 12V is 960W, so an inverter over 1000W will overload the cable, not to mention the other DC loads on your boat.

 

You need to consider if the cable is big enough. Also the main fuse must be below the 'weakest' cable capacity in your circuit, so check that as well.

This seems an unduly pessimistic rating, even in a poorly ventilated engine space, given that 35 Sq mm cable is nominally rated at 240 amps.
Link to comment
Share on other sites

GOOD DAY TO ALL RESPONDENTS,

THANKS FOR ALL THE RESPONSES TO MY QUESTION RE. BATTERY STRAPS.

I LIVE AND LEARN!!

 

SOOOO,

 

1) TO MIKE THE BOILERMAN. I EXPECTED MOST, IF NOT ALL, THE RECIPIENTS OF MY QUERY WOULD BE BOATERS AND IF AN UPPER CASE CORRESPONDENCE WITHOUT EXPLETIVES IS YOUR WORST EXPERIENCE THEN YOU ARE DOING VERY WELL smiley_offtopic.gif

YES, CATWEASEL, YOU ARE RIGHT LOTS OF SMALL SCREENS BEING USED.

 

2) THANKS TO ALL WHO GAVE A POSITIVE NO NONSENSE "DON'T DO IT" REPLY. PROBLEM NOW SORTED. clapping.gif

Link to comment
Share on other sites

GOOD DAY TO ALL RESPONDENTS,

THANKS FOR ALL THE RESPONSES TO MY QUESTION RE. BATTERY STRAPS.

I LIVE AND LEARN!!

 

SOOOO,

 

1) TO MIKE THE BOILERMAN. I EXPECTED MOST, IF NOT ALL, THE RECIPIENTS OF MY QUERY WOULD BE BOATERS AND IF AN UPPER CASE CORRESPONDENCE WITHOUT EXPLETIVES IS YOUR WORST EXPERIENCE THEN YOU ARE DOING VERY WELL smiley_offtopic.gif

YES, CATWEASEL, YOU ARE RIGHT LOTS OF SMALL SCREENS BEING USED.

 

2) THANKS TO ALL WHO GAVE A POSITIVE NO NONSENSE "DON'T DO IT" REPLY. PROBLEM NOW SORTED. clapping.gif

Those are the main points.

Thanks for the conclusion, many people don't bother.

Link to comment
Share on other sites

This seems an unduly pessimistic rating, even in a poorly ventilated engine space, given that 35 Sq mm cable is nominally rated at 240 amps.

According to AEI 2 cables close together in free air are rated at 162A, But at an ambient temperature of 60C the current should be derated by 0.5 giving 81A.

Obviously this is a continuous rating which is not probable on a boat, and 60C is possibly a bit high for the engine compartment, in which case the op can adjust up if justified.

 

http://www.aeicables.co.uk/literature/CurrentRatings.pdf

Edited by Chewbacka
Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.