Register now to gain access to all of our features. Once registered and logged in, you will be able to contribute to this site by submitting your own content or replying to existing content. You'll be able to customize your profile, receive reputation points as a reward for submitting content, while also communicating with other members via your own private inbox, plus much more!

This message will be removed once you have signed in.

Froggy

Advice sought re. battery replacement

165 posts in this topic

24 minutes ago, Chewbacka said:

Agreed, but could change depending upon what is plugged into your sockets.  For example some old SMPS will have capacitors between phase and earth and between neutral and earth to help soak up hf noise, so there is possibly a 'weak' reference to earth, so you might experience a bit of a shock if you touch things.   As they say on kids TV don't try this at home.

Indeed. My example was intended to explain the principle, not suggest a path for experimentation ;)

0

Share this post


Link to post
Share on other sites
16 minutes ago, Froggy said:

doesn't that .pdf Victron manual linked above make reference to earthing the unit?

Yes, because it has shore power coming into it. 

0

Share this post


Link to post
Share on other sites
5 minutes ago, WotEver said:

Precisely so. 

 

4 minutes ago, Chewbacka said:

Yes the RCD route is considered safer than a floating supply.  As briefly discussed above a floating supply is very safe but might with certain unusual appliance fault conditions be less safe than you would like.  As the people that write the regs have no control as to what you will plug into your system, they tend to specify considering 'worst case'.  As RCD's are now affordable and reliable the regs require them for new builds.  It's all about risk management.  As the nice lady from Victron told you, in the real world she has not heard of anyone being harmed by a floating system.  It is also a balance between cost, reliability and risk.  So a few years back the regs required a 10mA RCD in certain high risk locations on a boat, but I think that has now been dropped and 30mA is ok.  -  10mA will suffer from nuisance trips etc. far more so than 30mA.

Ok, fair enough, but at least i'm a little more reassured about our system being reasonably safe!

1 minute ago, WotEver said:

Yes, because it has shore power coming into it. 

D'oh! Yeah, of course! :wacko:

Well you've both been very helpful but nobody has replied re retro-adding an 'inverter' tag to this thread yet. All the information discussed might be helpful to others in the future.

0

Share this post


Link to post
Share on other sites
4 minutes ago, Froggy said:

Well you've both been very helpful but nobody has replied re retro-adding an 'inverter' tag to this thread yet. All the information discussed might be helpful to others in the future.

We've had many threads of a similar vein in the past and we're likely to have many more. A search will always find it but any future query is likely to be subtly different anyway. 

0

Share this post


Link to post
Share on other sites
Just now, WotEver said:

We've had many threads of a similar vein in the past and we're likely to have many more. A search will always find it but any future query is likely to be subtly different anyway. 

Ok. I'm just sending a quick query off to JD Narrowboats. If they reply and shed any further light on things i'll feed back on this thread.

0

Share this post


Link to post
Share on other sites
25 minutes ago, Froggy said:

Ok. I'm just sending a quick query off to JD Narrowboats. If they reply and shed any further light on things i'll feed back on this thread.

I doubt if they will say much more than - the inverter was fitted in compliance with the regs in force at the time and following normal industry practice.  Given that the Victron unit fitted can not by design have N&E bonded, then the fitting method seems to be reasonable.

0

Share this post


Link to post
Share on other sites
36 minutes ago, Chewbacka said:

I doubt if they will say much more than - the inverter was fitted in compliance with the regs in force at the time and following normal industry practice.  Given that the Victron unit fitted can not by design have N&E bonded, then the fitting method seems to be reasonable.

JD Narrowboats, from what I've read elsewhere on the forum, are quite well respected, as is the hull builder, Gary Gorton. It's nice to know that JD are still going, and i note from their website that they now build the hulls too.

0

Share this post


Link to post
Share on other sites

My hull is a Gary Gorton from 2001. Surveyor commented very favourably on it and said it was recognisable by the heart shaped holes at the top of the rudder and at the bottom of the gas locker in the bow.

0

Share this post


Link to post
Share on other sites
On 21/04/2017 at 17:34, Richard10002 said:

My hull is a Gary Gorton from 2001. Surveyor commented very favourably on it and said it was recognisable by the heart shaped holes at the top of the rudder and at the bottom of the gas locker in the bow.

Yes, that's exactly what our surveyor told us.  :)

0

Share this post


Link to post
Share on other sites
On 21/04/2017 at 14:37, Froggy said:

JD Narrowboats, from what I've read elsewhere on the forum, are quite well respected, as is the hull builder, Gary Gorton. It's nice to know that JD are still going, and i note from their website that they now build the hulls too.

Just to clarify this: the company that fitted our boat was actually JD Boat Services (Gailey), and NOT JD Narrowboats of Shardlow, which appears to be a completely different company. I learned this when i contacted the latter company and they got back to me saying that the hull couldn't possibly be theirs because they hadn't been gong that long! I then contacted JD Boat Services, and so far they haven't got back to me. It's possible that, although they still have a live website, they are no longer in business. JD Narrowboats build hulls and also do fitouts; JD Boat Services only do the latter.

Edited by Froggy
0

Share this post


Link to post
Share on other sites
4 minutes ago, Froggy said:

  It's possible that, although they still have a live website, they are no longer in business.

I think you will find they are,

0

Share this post


Link to post
Share on other sites

JD of Shardlow are quite recognisable by the front of the boat, virtually all have a single window and no doors.

They are flying out at present, some as sailaways, some fitted out locally and others being fitted out below Fradley.

Good luck to them. At least they are a decent shape.

0

Share this post


Link to post
Share on other sites
10 minutes ago, ditchcrawler said:

I think you will find they are,

Apart from the fact that they haven't got back to me so far, i did find it rather curious that, as boat fitters, their website shows mainly outside shots of boats they have worked on and very little illustration of their own work. The website also seems dated and photographs can't be shown in expanded view or as a slideshow, so it had me thinking that it might be an archived website. The quality of work on our boat, despite years of neglect by previous owners, was obviously of a reasonably high standard when originally commissioned, and some considerable thought seems to have gone into the design and execution of the layout (notwithstanding the fact that there aren't enough 240v sockets, including none in the aft room which doubles as a guest bedroom, yet one in the tiny corridor between it and the main bedroom that is partitioned by doors at both ends and gives access to the bathroom, suggesting that there was some failure to accurately co-ordinate the wiring circuit with the construction of the bulkheads! In fact there isn't a socket in the main bedroom either, but there's one just on the other side of the door that leads to the galley and saloon at the front of the boat :wacko: ).

Edited by Froggy
0

Share this post


Link to post
Share on other sites
2 minutes ago, Froggy said:

Apart from the fact that they haven't got back to me so far, i did find it rather curious that, as boat fitters, their website shows mainly outside shots of boats they have worked on and very little illustration of their own work. The website also seems dated and photographs can't be shown in expanded view or as a slideshow, so it had me thinking that it might be an archived website. The quality of work on our boat, despite years of neglect by previous owners, was obviously of a reasonably high standard when originally commissioned, and some considerable thought seems to have gone into the design and execution of the layout (notwithstanding the fact that there aren't enough 240v sockets, including none in the aft room which doubles as a guest bedroom, yet one in the tiny corridor between it and the main bedroom that is partitioned by doors at both ends and gives access to the bathroom, suggesting that there was some failure to accurately co-ordinate the wiring circuit with the construction of the bulkheads! In fact there isn't a socket in the main bedroom either, but there's one just on the other side of the door that leads to the galley and saloon at the front of the boat :wacko: ).

How old is the boat? maybe its what the first owner specified. I have two friends who once owned JD boats and were very pleased with them.

 

0

Share this post


Link to post
Share on other sites
1 hour ago, ditchcrawler said:

How old is the boat? maybe its what the first owner specified. I have two friends who once owned JD boats and were very pleased with them.

 

It's a 1997 build. It would be curious if the original owner wanted that electrical layout, where is the logic in having a socket in a small corridor between two rooms and another on the wrong side of the bedroom door? More likely imo that there was either an error of measurement or the owner changed their requirements with regard to bulkheads part-way through the work being done. It's the only criticism i can make about what's left of the original layout, which has been modified over time here and there such as bench seats being ripped out in the saloon to make it more open plan (JD supplied a detailed boat manual, so we can see the original layout from enclosed diagrams and descriptions). I'm certainly not displeased with what we bought except all the hidden costs that are due to neglect rather than design.

Just to make sure that we're not talking at odds, i am talking about JD Boat Services and not JD Narrowboats.

Edited by Froggy
0

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!


Register a new account

Sign in

Already have an account? Sign in here.


Sign In Now

  • Similar Content

    • By Pompey
      Hi All, 
      I have a ford 1.8xld with Bosch alternator, also the boat has a smith industries tacho, which has never been connected. I have searched and found links from other sites, as I understand it the Tacho is wired to ground and to the 'W' terminal of the alternator. See pics.
      As you can see from the alternator picture, the 'W' terminal appears to be missing, I am assuming that I will have to connect my own terminal her, probably by soldering. Is this correct ?
      The second picture is from the back of the Tacho. Assuming this is the wiring diagram, single ind is a single alternator setup, dual ind, for a dual alternator setup. So if I am reading correctly, 'W' connector from alternator, to pin 1 of Tacho, pin 2 of Tacho to Ground. And now if I wanted to connect the second Alternator, then the same for pins 3 and 4 ?
      If any one can just confirm or deny, been a while ( 18 years ) since working on this type of equipment. 
       


    • By jono2.0
      Hello,
       
      First post here so please be gentle! haha
       
      OK, I'm literally weeks away from getting my 60' sail away. I will be a continuous cruiser liveaboard and regularly moving around the canal and river waterways. Engine is a Canalline 42 with 1x 50A and 1x 175A Alternators. I'm planning on getting a Webasto water heater/boiler too to compliment multi fuel stove.
       
      I have done some sums and require around 120Ah a day for things like, 12v fridge, pumps, boiler, laptop, TV, lighting, phone charging etc. (Actual is 80Ah but I wanted a good amount of wiggle room).
       
      I'm planning on filling my roof with solar and would like to use Victron equipment (apart from solar).
       
      I'm planning on:
      5x 285w Monocrystalline Solar Panels totalling: 1425w (It has an approx 42' cabin / roof space) 1x Victron SmartSolar 100A MPPT Solar Charge Controller 1x Victron BMV-700 Battery Monitor 1x Victron SmartSolar LCD display 1x Victron Multiplus 1600VA Inverter 70A charger 16A relay 12V I'd like to use solar as much as possible to power my needs but haven't decided upon batteries just yet. I'd like your comments on qty and type of batteries I'd need to keep everything tip-top, if I'll need a generator for the winter months (likely Honda EU2.0i using LPG). Is the above all too overkill or will I struggle in the depths of dark winter? I would like to use a washing machine every so often but if batteries would get hammered I can use Generator for that. (obviously not on hot washes). I'll be getting an electrician to do the install (apart from solar panels on the roof). Thanks Jono
    • By Rob99fla
      Hi. Firstly, we are CC's with no hookup. I have a Victron 12/3000/120 inverter charger, Victron BMV602s battery monitor, 110amp alternator, Honda 1kw generator, Victron 30amp solar controller with 3x 100w solar panels. I have fitted 4x new Yuasa 115amp hr batteries. These are set as first set had faults within a few weeks (from Halfords are the batteries). When I charge the batteries from alternator, the BMV shows about 70amp initially and over a few hours reduces down to about 5-6 amp tail current. Charge voltage is about 14.3 volts. The BMV shows 100%. I always leave the engine running longer to see the tail current low as possible. I sometimes use the Honda generator to top up the batteries making sure they reach float status. Although the BMV shows say 70amps used since 100% charge and SOC still says about 90% charge, the battery voltage is down to below 12 volts. We have a 240v fridge freezer (new) running off the inverter plus some TV, led lights and phone charging, the actual current since last recharge (from the BMV) is correct I assume? Could it just be duff batteries again? Any ideas?
    • By Johny London
      I'm sure everyone remembers my poor charging regime and the lengthy thread that ensued.
       
      I'm still using my set of somewhat reduced capacity 4x110ah batteries - a couple hours engine running in the morning, a couple in the evening, and then switch off the 240v (including fridge) at night. This gives me enough laptop time in the evening, led lights and various pumps etc.
       
      So, for now carrying on quite happily - but I have noticed a new phenomenon creeping in lately.
       
      Today for example: I ran the engine for an hour or so when I got up (with 240v back on as normal). I then cruised for 3 1/2 hrs. A couple hours later, and my batteries are already back down to 12.3v so I have fired up the engine again.
       
      What I am saying is this - it would appear that the leisure batteries are not getting much (or any?) charge when I'm cruising. I can't think what this could be but I'm sure someone will enlighten me - be gentle!
       
      Just to re iterate - I know the batteries have reduced capacity, but a couple hours charging off the engine normally sees them up to say 12.8v which lasts all day or all evening. Even on longer cruises, they don't seem to get as much charge as when the engine is just running in neutral.
       
      I have two alternators, 50a for engine, 175 for leisure.
    • By guphware
      Hi all,
       
      We currently have 3 x 125ah leisure batteries powering the fridge, lighting (mostly LED) and water/waste pumps. The bank is charged by a single solar panel through an EPSolar MPPT charge controller. This was fine during the summer but with winter fast approaching we are finding that come the morning there isn't enough juice to power the pumps for a shower. We are mostly marina based so would like to add in a mains charger to top up the batteries once night falls. Electricity is metered so would only want to charge from shore power when necessary. Currently we achieve this by attaching a car battery charger using crocodile clips - it works but isn't a viable long term solution. The charger only has trickle or fast charge and is manually selected. I was also a little wary that I might be sending current to the solar panel instead of away from it, but it hasn't blown up yet
       
      So, my questions are:
      Is there such a device available that I can connect both the solar and a 240V charger to and it automatically selects which input to charge the batteries with, prioritising the solar? Maybe even with automatic health programming to allow the batteries to discharge periodically to keep them healthy? Failing that, if I just get a decent 240V charger that automatically switches charge mode, will there be any problems permanently connecting that directly to the batteries in addition to the solar, and just turn it on when required? Or should I connect them via, say, a rocker switch to manually change from solar charging or 240V charging? What fuses would be required? Can someone recommend a decent multistage 240V charger?  
      I'm sure I'll think of something else as soon as I've posted this, but it will do for starters :-) Thanks in advance.